When grid power goes out, all servers in a rack lose power immediately. The server administrator confirms the servers have dual power supplies, which are connected to separate PDUs. Each of the PDUs…

The correct answer is B. The power circuit was tripped on both PDUs. When both PDU circuits trip simultaneously during a power event, servers lose power immediately even though UPS devices are present, because power cannot flow through a tripped breaker.

Troubleshooting

Question

When grid power goes out, all servers in a rack lose power immediately. The server administrator confirms the servers have dual power supplies, which are connected to separate PDUs. Each of the PDUs is connected to a different UPS. Which of the following is the MOST likely cause of the problem?

Options

  • ABoth of the UPS devices were set for the wrong voltage.
  • BThe power circuit was tripped on both PDUs.
  • CThe server power supplies failed during the outage.
  • DThe UPS batteries were discharged.

How the community answered

(24 responses)
  • A
    13% (3)
  • B
    50% (12)
  • C
    8% (2)
  • D
    29% (7)

Why each option

When both PDU circuits trip simultaneously during a power event, servers lose power immediately even though UPS devices are present, because power cannot flow through a tripped breaker.

ABoth of the UPS devices were set for the wrong voltage.

Incorrect voltage settings would cause equipment damage or failure to power on initially, not a sudden loss of power coinciding precisely with a grid outage.

BThe power circuit was tripped on both PDUs.Correct

PDU circuit breakers can trip simultaneously during a power transient or surge that accompanies grid power loss, cutting the electrical path from the UPS devices to the servers. Even though UPS batteries may be charged and functioning, a tripped circuit on the PDU prevents power from reaching the server power supplies. This is the most likely single-event explanation for immediate, complete power loss across all servers despite the redundant UPS design.

CThe server power supplies failed during the outage.

Simultaneous failure of all server power supplies at the exact moment of a grid outage is statistically improbable and does not explain why both independent UPS devices provided no protection.

DThe UPS batteries were discharged.

Discharged UPS batteries would cause power loss as stored energy depleted, but the scenario describes immediate power loss rather than a gradual fade, making battery discharge a less likely cause than a tripped circuit.

Concept tested: Power redundancy failure analysis with UPS and PDU

Topics

#power redundancy#PDU#UPS#power failure