BICSI
RCDD-002 · Question #346
The owner's ICT distribution designer is forwarded an RFI from the ICT contractor requesting clarification on certification testing REQUIRED by the specifications for the horizontal cabling plant…
The correct answer is B. A level IIe field test instrument must be utilized. See the full explanation below for the reasoning.
Question
The owner’s ICT distribution designer is forwarded an RFI from the ICT contractor requesting clarification on certification testing REQUIRED by the specifications for the horizontal cabling plant. The contractor is asking for clarification and permission to submit a wire map test for a Cat6 installation. As the owner’s representative, how does the designer respond?
Options
- AA level III field test instrument must be utilized.
- BA level IIe field test instrument must be utilized.
- CFollow manufacturer recommendations as applicable and submit the results of the wire map
- DA level IIIe field test instrument must be utilized.
How the community answered
(17 responses)- A12% (2)
- B82% (14)
- C6% (1)
Community Discussion
No community discussion yet for this question.