RCDD-002 · Question #344
Which two of the following are fire protection considerations when designing telecommunications spaces? (Choose two.)
The correct answer is C. Drainage troughs can be placed under fire suppression sprinklers to protect telecommunications D. Only qualified installers should install approved firestop systems. See the full explanation below for the reasoning.
Question
Which two of the following are fire protection considerations when designing telecommunications spaces? (Choose two.)
Options
- ARequiring active sprinklers is one way to prevent water damage to equipment.
- BThe fire alarm system and other life safety systems shall not be contained in ERs due to the need
- CDrainage troughs can be placed under fire suppression sprinklers to protect telecommunications
- DOnly qualified installers should install approved firestop systems.
- ETo return penetrated walls, floors and ceilings to the hourly rating of the barrier, install conduit
How the community answered
(55 responses)- A4% (2)
- B7% (4)
- C73% (40)
- E16% (9)
Community Discussion
No community discussion yet for this question.