RCDD-002 · Question #341
RCDD-002 Question #341: Real Exam Question with Answer & Explanation
The correct answer is C. 7.75 dB. See the full explanation below for the reasoning.
Question
An ICT distribution designer installed a 62.5 mm/850 nm fiber optic cable from Building A to Building B with a distance of 1000 m (3280 ft). At Building B the designer fusion splice this new cable to an existing identical 62.5 mm fiber optic cable that runs 700 m (2300 ft) to Building C. Both ends are terminated with ST connectors. What is the WORST case loss budget for the above fiber link?
Options
- A6.20 dB
- B7 dB
- C7.75 dB
- D8.30 dB