RCDDV15 · Question #50
The ICT distribution designer is hired to design a Telecommunications Room on the third floor of a building. The size of the floor is 20 m by 26 m (92 x 85 It). What is to be the MINIMUM size of the…
The correct answer is B. =3 m (10 ft) by = 2.40 m (8 ft). Per ANSI/TIA-569 standards, a Telecommunications Room serving a floor area of 520 m² (the 20 x 26 m floor in this question) requires a minimum size of 3 m x 2.40 m (10 ft x 8 ft), which is option B - this dimension provides the baseline space needed for equipment racks, cable…
Question
The ICT distribution designer is hired to design a Telecommunications Room on the third floor of a building. The size of the floor is 20 m by 26 m (92 x 85 It). What is to be the MINIMUM size of the TR?
Options
- AShallow Room, no minimum room size
- B=3 m (10 ft) by = 2.40 m (8 ft)
- C=3 m (10 ft) by =2.74 m (9 ft)
- D=3 m (10 ft) by =3.40 m (11 ft)
How the community answered
(47 responses)- A17% (8)
- B70% (33)
- C9% (4)
- D4% (2)
Explanation
Per ANSI/TIA-569 standards, a Telecommunications Room serving a floor area of 520 m² (the 20 x 26 m floor in this question) requires a minimum size of 3 m x 2.40 m (10 ft x 8 ft), which is option B - this dimension provides the baseline space needed for equipment racks, cable management, and required working clearances. Option A is wrong because TIA-569 explicitly mandates minimum room dimensions for TRs; there is no "no minimum" provision. Option C (3 m x 2.74 m) and Option D (3 m x 3.40 m) are both larger than the code minimum for this floor area, and while larger rooms may be desirable, neither represents the minimum required by standard.
Memory tip: Remember "10 by 8" (10 ft wide, 8 ft deep) as the baseline TR minimum - the width of 10 ft accommodates a standard equipment rack row plus front and rear clearance, and 8 ft depth is the floor-size-dependent starting point that scales up only when the served area exceeds the threshold.