You are placing an entrance cable between two buildings connected by a conduit 205.3 m (588 ft) in length. What would be the MAXIMUM length of unlisted OSP cable that could be used before you terminat

The correct answer is C. 209 m (686 ft). Per NEC Section 800.154, unlisted outside plant (OSP) communications cable may extend a maximum of 15 m (50 ft) inside a building beyond the point of entry before it must be terminated or transitioned to a listed (plenum, riser, or general-purpose) cable. Because the conduit conn

Information Transport Systems (ITS) Distribution

Question

You are placing an entrance cable between two buildings connected by a conduit 205.3 m (588 ft) in length. What would be the MAXIMUM length of unlisted OSP cable that could be used before you terminate the cable or transition it to a listed cable?

Options

  • A185 m (607 ft)
  • B200 m (656 ft)
  • C209 m (686 ft)
  • D213 m (700 ft)
  • E216 m (708 ft)

How the community answered

(40 responses)
  • A
    3% (1)
  • B
    13% (5)
  • C
    75% (30)
  • D
    8% (3)
  • E
    3% (1)

Explanation

Per NEC Section 800.154, unlisted outside plant (OSP) communications cable may extend a maximum of 15 m (50 ft) inside a building beyond the point of entry before it must be terminated or transitioned to a listed (plenum, riser, or general-purpose) cable. Because the conduit connects TWO buildings, the cable enters and exits at both ends - so you add one 15 m (50 ft) indoor allowance for each building: 179 m (588 ft) conduit + 15 m (50 ft) at Building 1 + 15 m (50 ft) at Building 2 = 209 m (686 ft) total. Note: the metric value shown for the conduit length in the question (205.3 m) appears to be a typographical error; the operative figure is 588 ft (≈179 m).

Topics

#OSP cable#unlisted cable#entrance facility#NEC compliance