An isolated ground is used to:

The correct answer is C. Reduce EMI/RFI. An isolated ground outlet provides a dedicated, insulated ground return path that prevents common-mode noise coupling, specifically reducing EMI and RFI on sensitive electronic equipment.

Bonding, Grounding and Electrical Protection

Question

An isolated ground is used to:

Options

  • AReduce transients
  • BPrevent interruptions
  • CReduce EMI/RFI
  • DReduce swells and sags

How the community answered

(30 responses)
  • A
    7% (2)
  • B
    17% (5)
  • C
    70% (21)
  • D
    7% (2)

Why each option

An isolated ground outlet provides a dedicated, insulated ground return path that prevents common-mode noise coupling, specifically reducing EMI and RFI on sensitive electronic equipment.

AReduce transients

Transient suppression requires surge protection devices (SPDs) or UPS units with filtering; isolated grounds only provide a low-noise reference path and do not clamp voltage spikes.

BPrevent interruptions

Preventing power interruptions requires redundant supply paths or uninterruptible power supplies, which isolated grounds cannot provide.

CReduce EMI/RFICorrect

An isolated ground (IG) outlet, governed by NEC Article 250.146(D), runs an insulated ground conductor back to the panel without connecting to intermediate metallic enclosures, eliminating ground loops that would otherwise allow EMI and RFI to couple into equipment. This clean ground reference is critical for sensitive electronics such as computers and audio/video gear that are susceptible to noise on the ground plane. Isolated grounds do not regulate voltage magnitude, supply redundant power, or suppress transient spikes independently.

DReduce swells and sags

Swells and sags are RMS voltage magnitude variations corrected by voltage regulators or online UPS devices, not by grounding topology changes.

Concept tested: Isolated ground outlet function - EMI/RFI noise reduction

Source: https://www.nfpa.org/codes-and-standards/nfpa-70-national-electric-code-nec/70

Topics

#isolated ground#EMI/RFI reduction#noise mitigation#power quality