RCDD · Question #108
You are designing a firestop system for a hospital with several floors that have isolation rooms. Air leakage control is important to ensure rooms are sealed and restrict the spread of disease…
The correct answer is B. L rating. The L rating quantifies air leakage through a through-penetration firestop system and is the required rating when air containment is critical, such as in hospital isolation rooms.
Question
You are designing a firestop system for a hospital with several floors that have isolation rooms. Air leakage control is important to ensure rooms are sealed and restrict the spread of disease. Which firestop test rating should you use to ensure air leakage compliance?
Options
- AF rating
- BL rating
- CT rating
- DW rating
How the community answered
(22 responses)- A5% (1)
- B77% (17)
- C14% (3)
- D5% (1)
Why each option
The L rating quantifies air leakage through a through-penetration firestop system and is the required rating when air containment is critical, such as in hospital isolation rooms.
The F rating evaluates a firestop system's ability to resist flame passage and maintain structural integrity under fire conditions, with no measurement of air leakage at ambient or elevated temperatures.
The L rating, evaluated under UL 1479 and ASTM E283, measures the volume of air that passes through a through-penetration firestop assembly at both ambient temperature (L-ambient) and elevated temperature (L-400). For hospital isolation rooms that rely on negative or positive pressure to contain airborne pathogens and prevent cross-contamination between spaces, specifying a firestop system with a verified L rating ensures that cable and conduit penetrations do not undermine the room's pressure boundary and infection control design.
The T rating measures the temperature rise on the unexposed side of a firestop assembly to assess thermal transfer performance, which is unrelated to air leakage or pressure containment.
The W rating assesses a firestop system's resistance to water penetration under hydrostatic pressure, and has no relevance to air leakage or room air pressure control.
Concept tested: Firestop L rating for air leakage and pressure control
Source: https://ulstandards.ul.com/standard/?id=1479_6