RCDD · Question #251

You are designing an audible alarm notification system for an office environment with an ambient noise level of 55 dBA. What dBA level should the horn be set at?

The correct answer is E. 70 dBA. NFPA 72 mandates that audible notification appliances produce a sound level at least 15 dBA above the ambient noise level, so a 55 dBA environment requires a minimum horn output of 70 dBA.

Emergency, Life Safety and Security

Question

You are designing an audible alarm notification system for an office environment with an ambient noise level of 55 dBA. What dBA level should the horn be set at?

Options

  • A40 dBA
  • B50 dBA
  • C55 dBA
  • D65 dBA
  • E70 dBA

How the community answered

(19 responses)
  • A
    16% (3)
  • B
    5% (1)
  • D
    5% (1)
  • E
    74% (14)

Why each option

NFPA 72 mandates that audible notification appliances produce a sound level at least 15 dBA above the ambient noise level, so a 55 dBA environment requires a minimum horn output of 70 dBA.

A40 dBA

40 dBA is 15 dBA below the ambient noise level, meaning the alarm would be completely masked and inaudible in the 55 dBA environment.

B50 dBA

50 dBA is 5 dBA below ambient and is still masked by background noise, failing the NFPA 72 requirement of being at least 15 dBA above ambient.

C55 dBA

55 dBA equals the ambient level and provides zero audible margin above background noise, falling far short of the 15 dBA above ambient requirement.

D65 dBA

65 dBA is only 10 dBA above the 55 dBA ambient level, which is insufficient and does not meet the NFPA 72 minimum margin of 15 dBA above ambient.

E70 dBACorrect

Per NFPA 72, audible notification appliances must emit a sound pressure level of at least 15 dBA above the average ambient sound level measured in the occupiable area. Adding 15 dBA to the 55 dBA ambient level yields the required minimum of 70 dBA at the device. This margin ensures the alarm signal remains clearly distinguishable above background noise and audible to occupants throughout the space.

Concept tested: NFPA 72 audible alarm sound level above ambient requirement

Source: https://www.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=72

Topics

#audible alarm#notification appliance#dBA level#fire alarm