You have discovered a common mode current on the metallic cable sheaths of your building riser cables. What is the MOST likely cause for you to investigate?

The correct answer is B. Two separate and distinct ground references. Common mode current on cable sheaths is the classic symptom of a ground loop, which occurs when two separate ground references have different electrical potentials.

Bonding, Grounding and Electrical Protection

Question

You have discovered a common mode current on the metallic cable sheaths of your building riser cables. What is the MOST likely cause for you to investigate?

Options

  • ALack of cable protection
  • BTwo separate and distinct ground references
  • CImproper secondary protection
  • DImproper physical protection of cable
  • EImproper placement and/or termination of cables

How the community answered

(39 responses)
  • A
    5% (2)
  • B
    74% (29)
  • C
    3% (1)
  • D
    15% (6)
  • E
    3% (1)

Why each option

Common mode current on cable sheaths is the classic symptom of a ground loop, which occurs when two separate ground references have different electrical potentials.

ALack of cable protection

Lack of cable protection addresses physical damage such as crushing or abrasion and has no relationship to the generation of common mode currents on metallic sheaths.

BTwo separate and distinct ground referencesCorrect

When two physically separate ground references exist in a building, a difference in electrical potential almost always exists between them. That potential difference drives current through the metallic cable sheath, which becomes an unintended return conductor between the two grounds, producing the observed common mode current. Resolving this requires establishing a single-point or equipotential bonding ground system to eliminate the voltage difference.

CImproper secondary protection

Improper secondary protection refers to inadequate surge or lightning protection devices and does not explain steady-state common mode current on riser cable sheaths.

DImproper physical protection of cable

Improper physical protection concerns mechanical damage prevention and does not produce the electromagnetic condition of common mode sheath current.

EImproper placement and/or termination of cables

Improper placement or termination may cause crosstalk or signal integrity problems but is not the root cause of common mode current flowing on cable sheaths.

Concept tested: Common mode current cause - ground loop from multiple references

Topics

#common mode current#ground reference#cable sheath#bonding