RCDD-002 · Question #71
The size and number of conduits or sleeves used for backbone pathways depend on the usable floor space served by the backbone distribution system. What is the MINIMUM trade size of sleeves…
The correct answer is B. 4. According to ANSI/TIA-568 and BICSI backbone pathway standards, a minimum trade size of 4 (4-inch diameter) is required for sleeves serving a TR, ER, or EF because backbone pathways must accommodate multiple large cable bundles - including copper, fiber, and coax - with…
Question
The size and number of conduits or sleeves used for backbone pathways depend on the usable floor space served by the backbone distribution system. What is the MINIMUM trade size of sleeves recommended to serve a TR, ER, or EF?
Options
- A2
- B4
- C6
- D8
How the community answered
(21 responses)- B86% (18)
- C5% (1)
- D10% (2)
Explanation
According to ANSI/TIA-568 and BICSI backbone pathway standards, a minimum trade size of 4 (4-inch diameter) is required for sleeves serving a TR, ER, or EF because backbone pathways must accommodate multiple large cable bundles - including copper, fiber, and coax - with sufficient fill capacity and room for future growth that smaller conduits simply cannot support.
Option A (trade size 2) is wrong because 2-inch sleeves are appropriate for horizontal pathways or smaller inter-room runs, not the high-capacity backbone distribution entering or leaving a telecommunications space. Options C and D (trade sizes 6 and 8) are not wrong in practice - larger is acceptable - but they exceed the minimum requirement the question asks for, making them incorrect answers here.
Memory tip: Think "4 for the floor" - trade size 4 is the floor (minimum) for backbone sleeves entering major telecom spaces. If you remember that backbone = bigger than horizontal (which uses smaller conduits), and the minimum jumps to 4, you'll lock in the right answer.
Topics