1Z0-902 · Question #29
A new Exadata Quarter Rack with 2 Database Servers and 3 HC Storage Servers and 3-phase 15kVA PDUs is being installed in a Data Center. However, the Data Center is only providing enough power for a…
The correct answer is A. The installation can go ahead, no change is required. According to the Oracle Exadata Database Machine X9M-2 Data Sheet, each PDU has two power input cables that can be connected to separate power sources for redundancy. However, if only one power source is available per PDU, then a single cable can be used to provide sufficient…
Question
A new Exadata Quarter Rack with 2 Database Servers and 3 HC Storage Servers and 3-phase 15kVA PDUs is being installed in a Data Center. However, the Data Center is only providing enough power for a single cable from each PDU. Which statement is correct?
Options
- AThe installation can go ahead, no change is required.
- BThe installation cannot proceed until two power feeds are available per PDU.
- CA splitter cable can be used to provide power to all PDU cables.
- DThe power cables from the servers to the PDUs can be rearranged inside the rack following OECA
How the community answered
(34 responses)- A85% (29)
- B3% (1)
- C3% (1)
- D9% (3)
Explanation
According to the Oracle Exadata Database Machine X9M-2 Data Sheet, each PDU has two power input cables that can be connected to separate power sources for redundancy. However, if only one power source is available per PDU, then a single cable can be used to provide sufficient power for normal operation.
Topics
Community Discussion
No community discussion yet for this question.