RCDDV15 · Question #80
When designing for horizontal pathways in an environment that requires fire-stopping for penetrating a rated wall, what is the MAXIMUM till ratio for telecommunications cabling in a cable tray?
The correct answer is B. 40 percent. When telecommunications cable trays penetrate a fire-rated wall, the maximum allowable fill ratio is 40 percent, as required to ensure that approved fire-stop materials can be properly installed around the cables and within the tray to maintain the wall's fire rating integrity…
Question
When designing for horizontal pathways in an environment that requires fire-stopping for penetrating a rated wall, what is the MAXIMUM till ratio for telecommunications cabling in a cable tray?
Options
- A20 percent
- B40 percent
- C50 percent
- DThere is no fill ratio for cable tray
How the community answered
(27 responses)- A4% (1)
- B81% (22)
- C4% (1)
- D11% (3)
Explanation
When telecommunications cable trays penetrate a fire-rated wall, the maximum allowable fill ratio is 40 percent, as required to ensure that approved fire-stop materials can be properly installed around the cables and within the tray to maintain the wall's fire rating integrity.
Option A (20 percent) is incorrect because it is overly restrictive and not the standard specified for this application. Option C (50 percent) is a common fill ratio referenced for general cable tray installations, but it does not account for the added requirement of accommodating fire-stopping compounds at rated wall penetrations. Option D is incorrect because fire-stopping requirements do impose a fill limit precisely to ensure the intumescent or sealant material can fully encapsulate the cables and seal the opening effectively.
Memory tip: Associate "40 for fire" - when a wall is rated, you drop from the general 50 percent fill guidance down to 40 percent to leave room for the fire-stop material to do its job.
Topics
Community Discussion
No community discussion yet for this question.