An ICT distribution designer is providing labeling for a data center room number 2A, located on the second floor having 10 rows of cabinets. Which of the following identifiers/labels would the…
The correct answer is B. 2A-SBB/R601.1. See the full explanation below for the reasoning.
Grounding and Bonding
Question
An ICT distribution designer is providing labeling for a data center room number 2A, located on the second floor having 10 rows of cabinets. Which of the following identifiers/labels would the designer attach to the bonding and grounding conductor between the first cabinet in the 6th row and the data center ground bar?
Options
- A2A/R601.1
- B2A-SBB/R601.1
- C2/R6
- DTEF1/R601.1
How the community answered
(42 responses)- A5% (2)
- B71% (30)
- C14% (6)
- D10% (4)
Topics
#data center labeling#grounding conductor#bonding identification#data center infrastructure