When designing a campus distribution system involving small buildings with only one horizontal cross-connect (HC) [Floor distributor (FD)] per building, you can eliminate the need for a(n):

The correct answer is A. Intermediate cross-connect (IC) Building distributor (BD). In the structured cabling hierarchy, when a small building contains only one horizontal cross-connect (HC/FD), the intermediate cross-connect (IC) or building distributor (BD) level can be eliminated, allowing the FD to connect directly to the campus distributor.

Information Transport Systems (ITS) Distribution

Question

When designing a campus distribution system involving small buildings with only one horizontal cross-connect (HC) [Floor distributor (FD)] per building, you can eliminate the need for a(n):

Options

  • AIntermediate cross-connect (IC) Building distributor (BD)
  • BMain cross-connect (MC) Campus distributor (CD)
  • CHorizontal cross-connect (HC) Floor distributor (FD)
  • DEntrance facility (EF)
  • ELatching connector (LC)

How the community answered

(26 responses)
  • A
    73% (19)
  • C
    8% (2)
  • D
    15% (4)
  • E
    4% (1)

Why each option

In the structured cabling hierarchy, when a small building contains only one horizontal cross-connect (HC/FD), the intermediate cross-connect (IC) or building distributor (BD) level can be eliminated, allowing the FD to connect directly to the campus distributor.

AIntermediate cross-connect (IC) Building distributor (BD)Correct

TIA-568 and ISO 11801 permit the elimination of the intermediate cross-connect (IC) - called the building distributor (BD) in ISO terminology - when a building contains only a single horizontal cross-connect (floor distributor). In this scenario, the HC/FD connects directly to the main cross-connect (MC) or campus distributor (CD), simplifying the cabling hierarchy without violating standards requirements.

BMain cross-connect (MC) Campus distributor (CD)

The main cross-connect (MC) or campus distributor (CD) is the top-level aggregation point for the campus backbone and cannot be eliminated; it is required to interconnect all buildings in the campus distribution system.

CHorizontal cross-connect (HC) Floor distributor (FD)

The horizontal cross-connect (HC) or floor distributor (FD) is the central premise of this scenario - the building has exactly one - and it cannot be eliminated because it serves as the termination point for horizontal cabling to work areas.

DEntrance facility (EF)

The entrance facility (EF) is required wherever outside plant cables enter a building and cannot be removed from a campus distribution design regardless of building size.

ELatching connector (LC)

A latching connector (LC) is a fiber optic connector type (small form factor), not a hierarchical cross-connect level in the structured cabling topology, making it irrelevant to this design decision.

Concept tested: Eliminating intermediate cross-connect in single-HC building design

Topics

#campus distribution#intermediate cross-connect#building distributor#backbone hierarchy