Cables are installed in a ceiling in a straight line. The ceiling run is 60 m (200 ft) in length. What is the MINIMUM number of J-hooks required to support the cables?
The correct answer is C. 40. J-hooks must be placed at a maximum interval of 1.5 m (5 ft) along a cable run, so a 60 m (200 ft) run requires a minimum of 200 divided by 5 equals 40 J-hooks. Fewer hooks would violate the maximum spacing requirement; more hooks exceed the minimum.
Question
Cables are installed in a ceiling in a straight line. The ceiling run is 60 m (200 ft) in length. What is the MINIMUM number of J-hooks required to support the cables?
Options
- A20
- B30
- C40
- D50
- E60
How the community answered
(26 responses)- B4% (1)
- C73% (19)
- D15% (4)
- E8% (2)
Why each option
J-hooks must be placed at a maximum interval of 1.5 m (5 ft) along a cable run, so a 60 m (200 ft) run requires a minimum of 200 divided by 5 equals 40 J-hooks. Fewer hooks would violate the maximum spacing requirement; more hooks exceed the minimum.
20 J-hooks results in 10 ft spacing between supports, which more than doubles the 5 ft maximum allowed interval and would cause excessive cable sag and potential conductor damage.
30 J-hooks produces approximately 6.7 ft spacing, which still exceeds the maximum 1.5 m (5 ft) spacing standard and does not provide adequate cable support.
BICSI TDMM and TIA-569 specify that J-hooks supporting horizontal copper or fiber cables must be installed at intervals not exceeding 1.5 m (5 ft) to prevent cable sag, jacket deformation, and bend radius violations. Dividing the 200 ft run by the 5 ft maximum spacing yields exactly 40 J-hooks as the minimum compliant count. Installing fewer than 40 would result in spans longer than 5 ft, which fails the support spacing requirement.
50 J-hooks would place supports every 4 ft, which is valid for cable support but exceeds the minimum required count - the question asks for the minimum, which is 40.
60 J-hooks places supports every 3.3 ft, which is a permitted spacing but represents more than the minimum needed, adding unnecessary material and labor cost.
Concept tested: J-hook maximum spacing for horizontal cable support