RCDD · Question #45
In the ceiling zone method of distribution, the usable floor area should be divided into zones each measuring:
The correct answer is C. 23 sq m (250 sq ft) to 84 sq m (904 sq ft). In the ceiling zone method, each zone of usable floor area must measure between 23 sq m (250 sq ft) and 84 sq m (904 sq ft) per BICSI TDMM guidelines. This range balances practical cable reach from a zone enclosure with efficient floor coverage.
Question
In the ceiling zone method of distribution, the usable floor area should be divided into zones each measuring:
Options
- A9.3 sq m (100 sq ft) to 23 sq m (250 sq ft)
- B23 sq m (250 sq ft) to 56 sq m (600 sq ft)
- C23 sq m (250 sq ft) to 84 sq m (904 sq ft)
- D56 sq m (600 sq ft) to 84 sq m (904 sq ft)
- E56 sq m (600 sq ft) to 100 sq m (1,100 sq ft)
How the community answered
(51 responses)- A6% (3)
- B2% (1)
- C80% (41)
- D10% (5)
- E2% (1)
Why each option
In the ceiling zone method, each zone of usable floor area must measure between 23 sq m (250 sq ft) and 84 sq m (904 sq ft) per BICSI TDMM guidelines. This range balances practical cable reach from a zone enclosure with efficient floor coverage.
9.3-23 sq m (100-250 sq ft) defines zones that are too small, which would require an impractical number of zone enclosures per floor and drives up cost unnecessarily.
23-56 sq m (250-600 sq ft) only covers the lower half of the permitted range and incorrectly excludes valid zones up to 84 sq m (904 sq ft) allowed by BICSI standards.
BICSI TDMM specifies that ceiling zone distribution zones must range from 23 sq m (250 sq ft) to 84 sq m (904 sq ft) to ensure cables from a zone enclosure or consolidation point can adequately serve all workstations within the zone. Zones smaller than 23 sq m create an excessive number of distribution points, while zones larger than 84 sq m exceed the practical horizontal cable reach from a single overhead enclosure. This range optimizes both infrastructure cost and cabling flexibility.
56-84 sq m (600-904 sq ft) captures only the upper portion of the permitted range and incorrectly excludes zones as small as 23 sq m (250 sq ft) from consideration.
56-100 sq m (600-1,100 sq ft) exceeds the BICSI maximum zone ceiling of 84 sq m (904 sq ft), which would cause horizontal cabling to exceed manageable distribution distances from a single overhead enclosure.
Concept tested: Ceiling zone method zone area sizing