RCDD · Question #349
A furniture cluster with 26 requires a MINIMUM of how many multiuser telecommunications outlet assembly (MUTOA)?
The correct answer is C. 3. Per ANSI/TIA-568 standards, a single MUTOA can serve a maximum of 12 work areas. For a furniture cluster with 26 work areas: 26 ÷ 12 = 2.17, which must be rounded up to the next whole number. Therefore, a minimum of 3 MUTOAs are required. Two MUTOAs would only cover 24 work areas
Question
A furniture cluster with 26 requires a MINIMUM of how many multiuser telecommunications outlet assembly (MUTOA)?
Options
- A1
- B2
- C3
- D4
- E5
How the community answered
(49 responses)- A12% (6)
- B2% (1)
- C73% (36)
- D8% (4)
- E4% (2)
Explanation
Per ANSI/TIA-568 standards, a single MUTOA can serve a maximum of 12 work areas. For a furniture cluster with 26 work areas: 26 ÷ 12 = 2.17, which must be rounded up to the next whole number. Therefore, a minimum of 3 MUTOAs are required. Two MUTOAs would only cover 24 work areas (2 × 12 = 24), which is insufficient for 26. Three MUTOAs provide capacity for up to 36 work areas, satisfying the requirement.