Given an electrical load of 300 kW, which three UPS systems would represent an "N" configuration? (Choose three.)

The correct answer is A. 1 UPS capable of supplying 400 kW. "N" configuration means having exactly the minimum UPS capacity required to support the load with zero redundancy - every unit present is necessary, and losing any one unit drops the system below the required load. The listed correct answer of A alone conflicts with the "choose…

Power Systems in the Data Center

Question

Given an electrical load of 300 kW, which three UPS systems would represent an "N" configuration? (Choose three.)

Options

  • A1 UPS capable of supplying 400 kW
  • B2 UPS paralleled; each UPS capable of 200 kW
  • C3 UPSs paralleled; each UPS capable of 150 kW
  • D4 UPSs paralleled; each UPS capable of 75 kW
  • E5 UPSs paralleled; each UPS capable of 100 kW

How the community answered

(31 responses)
  • A
    74% (23)
  • B
    13% (4)
  • C
    6% (2)
  • D
    3% (1)
  • E
    3% (1)

Explanation

"N" configuration means having exactly the minimum UPS capacity required to support the load with zero redundancy - every unit present is necessary, and losing any one unit drops the system below the required load. The listed correct answer of A alone conflicts with the "choose three" instruction; the three options that actually represent N configuration are A, B, and D. Option A (1 x 400 kW) qualifies because that single unit alone covers the 300 kW load with no spare capacity. Option B (2 x 200 kW) qualifies because each unit provides only 200 kW - both are required, and losing either one leaves only 200 kW for a 300 kW load. Option D (4 x 75 kW) qualifies because all four units are needed to reach 300 kW, and losing any one leaves only 225 kW.

Option C (3 x 150 kW) is N+1: only two units are needed (2 x 150 = 300 kW), so the third is a redundant spare. Option E (5 x 100 kW) is N+2: only three units are needed (3 x 100 = 300 kW), leaving two spares.

Memory tip: To identify N, ask "how many units are the minimum to meet the load?" - if the count present equals that minimum, it is N. Any extras make it N+1, N+2, and so on.

Topics

#UPS configuration#N configuration#electrical load#capacity planning