A company wants to build a data center infrastructure which can provide up to 99.982% uptime availability per year. Which ANSI/TIA-942 data center tier meets the requirement?

The correct answer is C. Concurrently maintainable site infrastructure. ANSI/TIA-942 Tier 3 (Concurrently Maintainable) defines 99.982% uptime, allowing maintenance on any component without requiring a data center shutdown.

Service-Related Knowledge

Question

A company wants to build a data center infrastructure which can provide up to 99.982% uptime availability per year. Which ANSI/TIA-942 data center tier meets the requirement?

Options

  • ARedundant-distribution site infrastructure
  • BRedundant-capacity component site infrastructure
  • CConcurrently maintainable site infrastructure
  • DBasic site infrastructure

How the community answered

(42 responses)
  • A
    5% (2)
  • B
    2% (1)
  • C
    83% (35)
  • D
    10% (4)

Why each option

ANSI/TIA-942 Tier 3 (Concurrently Maintainable) defines 99.982% uptime, allowing maintenance on any component without requiring a data center shutdown.

ARedundant-distribution site infrastructure

Redundant-distribution site infrastructure is not a recognized ANSI/TIA-942 tier name; this phrase does not correspond to any of the four defined tiers in the standard.

BRedundant-capacity component site infrastructure

Redundant-capacity component site infrastructure describes Tier 2, which delivers only 99.741% availability - significantly below the 99.982% requirement specified in the question.

CConcurrently maintainable site infrastructureCorrect

Tier 3 - Concurrently Maintainable site infrastructure - is specified by ANSI/TIA-942 as providing 99.982% availability (roughly 1.6 hours of downtime per year), achieved through N+1 redundant power and cooling delivery paths that allow planned maintenance to occur without interrupting active IT operations.

DBasic site infrastructure

Basic site infrastructure is Tier 1, providing only 99.671% availability with no redundant components, making it far short of the 99.982% uptime target.

Concept tested: ANSI/TIA-942 data center tier availability percentages

Source: https://www.tiaonline.org/all-standards/tia-942-b/

Topics

#ANSI/TIA-942#data center tiers#uptime availability#concurrent maintainability