Which of the following is TRUE for tele communications spaces?

The correct answer is B. Plumbing piping not related to the support of the space should not pass through the space. Option B is correct because telecommunications spaces (equipment rooms and telecommunications rooms) must be protected from water damage - any plumbing unrelated to the space's own support functions (e.g., HVAC condensate) should be routed around, not through, the space, per…

Telecommunications Infrastructure Planning and Design

Question

Which of the following is TRUE for tele communications spaces?

Options

  • AMaintain aim (3.28 ft) clearance between equipment and plumbing fixtures such as mop sinks
  • BPlumbing piping not related to the support of the space should not pass through the space.
  • CRelative humidity snail be maintained at 40% ?5%.
  • DClose proximity to water service is desired so consider locating the ER in the pipe chase.

How the community answered

(27 responses)
  • A
    19% (5)
  • B
    70% (19)
  • C
    4% (1)
  • D
    7% (2)

Explanation

Option B is correct because telecommunications spaces (equipment rooms and telecommunications rooms) must be protected from water damage - any plumbing unrelated to the space's own support functions (e.g., HVAC condensate) should be routed around, not through, the space, per ANSI/TIA-569 standards.

Why the distractors are wrong:

  • A is incorrect because the standard does not require a 1m (3.28 ft) clearance between equipment and mop sinks - it prohibits unrelated plumbing entirely, making proximity to a mop sink a non-starter.
  • C is incorrect on the numbers; applicable standards (ASHRAE/TIA) typically specify a relative humidity range of approximately 30–55%, not the narrow 40% ±5% band stated.
  • D is the opposite of correct practice - locating an equipment room in a pipe chase deliberately places sensitive electronics adjacent to water supply lines, maximizing leak risk.

Memory tip: Think of a telecom room as hydrophobic - it fears water. The rule is simple: if a pipe has no business being there, it shouldn't be there. Any answer suggesting water proximity is "desired" is an automatic red flag.

Topics

#Telecom Room Standards#Equipment Space Protection#Building Systems Integration#Facility Design