BICSI
RCDDV15 · Question #260
For a backbone distribution system serving a usable floor space of 8,920 m2 (96,000 ft2), the MINIMUM slot area to be used for this back bone is
The correct answer is B. 0.048 m2 (72 in2). See the full explanation below for the reasoning.
Backbone Distribution Design
Question
For a backbone distribution system serving a usable floor space of 8,920 m2 (96,000 ft2), the MINIMUM slot area to be used for this back bone is
Options
- A0.040 m2 (60 in2)
- B0.048 m2 (72 in2)
- C0.056 m2 (84 in2)
- D0.064 m2 (96 in2)
How the community answered
(20 responses)- A5% (1)
- B70% (14)
- C10% (2)
- D15% (3)
Topics
#backbone distribution#slot area calculation#pathway sizing#floor space ratio