RCDD · Question #83
You are starting work on a new high school. The architect has provided you with a telecommunications room located between the kitchen cold store room and the automotive and welding shops. What…
The correct answer is A. Work with the architect to find another location. Telecommunications rooms must not be sited adjacent to strong electromagnetic interference sources such as refrigeration compressors and arc welding equipment, and the correct resolution is to relocate the space during the design phase.
Question
You are starting work on a new high school. The architect has provided you with a telecommunications room located between the kitchen cold store room and the automotive and welding shops. What should you do?
Options
- AWork with the architect to find another location
- BInsist that the welding shop be placed as far from the telecommunications space as possible
- CFile a complaint with the client
- DProvide shielded cable tray in the telecommunications room and in the outer halls
- ERequest that shielding be placed around the compressors and the arc welding units
How the community answered
(26 responses)- A77% (20)
- C8% (2)
- D12% (3)
- E4% (1)
Why each option
Telecommunications rooms must not be sited adjacent to strong electromagnetic interference sources such as refrigeration compressors and arc welding equipment, and the correct resolution is to relocate the space during the design phase.
Working with the architect to find a new location is the correct and most cost-effective solution because placing a telecommunications room between a kitchen cold store (compressor EMI) and a welding shop (arc welding EMI) violates structured cabling best practices for EMI-free telecommunications spaces. Mitigating EMI after room placement is far more expensive and less reliable than choosing an appropriate location during design. BICSI and ANSI/TIA-569 specify that telecommunications spaces must be separated from known sources of electromagnetic and radio frequency interference.
Insisting only the welding shop be moved does not address the EMI risk from the kitchen cold store compressors and fails to fully resolve the improper room placement.
Filing a complaint with the client is not a constructive technical solution and does not resolve the EMI hazard posed by the adjacent mechanical and industrial spaces.
Shielded cable tray in the room and outer halls is insufficient to mitigate the intense EMI generated by arc welding equipment and refrigeration compressors at close proximity.
Requesting shielding around compressors and welding units is impractical, prohibitively expensive, and not a recognized standard solution for protecting telecommunications infrastructure from EMI.
Concept tested: Telecommunications room placement and EMI source avoidance
Source: https://tiaonline.org/what-we-do/standards/
Topics