RCDD-001 · Question #82

You are placing two 423 mm (19 in) relay racks with a 152 mm (6 in) vertical management panel on each end and a 12 in vertical cable management panel between the racks. The rack lineup begins…

The correct answer is D. 2.4 m (8 ft) x 3.0 m (10 ft). See the full explanation below for the reasoning.

Question

You are placing two 423 mm (19 in) relay racks with a 152 mm (6 in) vertical management panel on each end and a 12 in vertical cable management panel between the racks. The rack lineup begins against a wall in the room. What is the MINIMUM room size required?

Options

  • A1.83 m (6 ft) x 2.4 m (8 ft)
  • B2.1 m (7 ft) x 2.4 m (8 ft)
  • C2.4 m (8 ft) x 2.4 m (8 ft)
  • D2.4 m (8 ft) x 3.0 m (10 ft)
  • E3.0 m (10 ft) x 3.0 m (10 ft)

How the community answered

(58 responses)
  • A
    5% (3)
  • B
    2% (1)
  • C
    9% (5)
  • D
    83% (48)
  • E
    2% (1)