RCDD-001 · Question #47
You are designing a horizontal distribution system that will have a zone box located 71.6 m (235 ft) away from the telecommunications room (TR). A 50 mm (2 in) conduit is designed from the TR to a…
The correct answer is B. 3. See the full explanation below for the reasoning.
Question
You are designing a horizontal distribution system that will have a zone box located 71.6 m (235 ft) away from the telecommunications room (TR). A 50 mm (2 in) conduit is designed from the TR to a pull box located 36.6 m (120 ft) away from the TR. A 1 1/2 inch conduit is designed from the pull box to the zone box located 35.1 m (115 ft) beyond the pull box. Assuming no conduit bends, and excluding the TR and zone box, what is the total number of pull boxes/pull points required in this horizontal conduit system between the telecommunications room (TR) and zone box?
Options
- A2
- B3
- C4
- D5
How the community answered
(44 responses)- A11% (5)
- B77% (34)
- C9% (4)
- D2% (1)
Community Discussion
No community discussion yet for this question.