RCDD-001 · Question #47

You are designing a horizontal distribution system that will have a zone box located 71.6 m (235 ft) away from the telecommunications room (TR). A 50 mm (2 in) conduit is designed from the TR to a…

The correct answer is B. 3. See the full explanation below for the reasoning.

Question

You are designing a horizontal distribution system that will have a zone box located 71.6 m (235 ft) away from the telecommunications room (TR). A 50 mm (2 in) conduit is designed from the TR to a pull box located 36.6 m (120 ft) away from the TR. A 1 1/2 inch conduit is designed from the pull box to the zone box located 35.1 m (115 ft) beyond the pull box. Assuming no conduit bends, and excluding the TR and zone box, what is the total number of pull boxes/pull points required in this horizontal conduit system between the telecommunications room (TR) and zone box?

Options

  • A2
  • B3
  • C4
  • D5

How the community answered

(44 responses)
  • A
    11% (5)
  • B
    77% (34)
  • C
    9% (4)
  • D
    2% (1)

Community Discussion

No community discussion yet for this question.