You are placing an entrance cable between two buildings connected by a conduit 205.3 m (588 ft) in length. What would be the MAXIMUM length of unlisted OSP cable that could be used before you…
The correct answer is C. 209 m (686 ft). See the full explanation below for the reasoning.
Question
You are placing an entrance cable between two buildings connected by a conduit 205.3 m (588 ft) in length. What would be the MAXIMUM length of unlisted OSP cable that could be used before you terminate the cable or transition it to a listed cable?
Options
- A185 m (607 ft)
- B200 m (656 ft)
- C209 m (686 ft)
- D213 m (700 ft)
- E216 m (708 ft)
How the community answered
(53 responses)- A9% (5)
- B2% (1)
- C79% (42)
- D8% (4)
- E2% (1)