An outside plant (OSP) cable must be placed under a pipeline with two side by side pipe runs. The distance between the outside pipes is 6 m (20 ft). What is the length of the conduit required to…

The correct answer is E. 12 m (40 ft). See the full explanation below for the reasoning.

Question

An outside plant (OSP) cable must be placed under a pipeline with two side by side pipe runs. The distance between the outside pipes is 6 m (20 ft). What is the length of the conduit required to facilitate the pipeline crossing?

Options

  • A6 m (20 ft)
  • B7.6 m (25 ft)
  • C9 m (30 ft)
  • D10.7 m (35 ft)
  • E12 m (40 ft)

How the community answered

(52 responses)
  • A
    8% (4)
  • B
    15% (8)
  • C
    2% (1)
  • D
    2% (1)
  • E
    73% (38)