You are preparing to test newly installed open office cabling. Within the open office cabling, there are multiple consolidation points (CP) that were installed while waiting for furniture. How do you proceed with permanent link testing?
Options
- ATest to each CP, then test from CP to workstation.
- BWait for open office cabling to be completed, then test to each workstation outlet, including the CP.
- CTest that the CP is within 90 meters, then test again to the workstation outlet.
- DPerform permanent link tests to each CP, then continuity tests from CP to each workstation outlet.
- ETest to each workstation outlet, treating each outlet as a channel.
How the community answered
(30 responses)- A7% (2)
- B73% (22)
- C3% (1)
- D13% (4)
- E3% (1)