What is the worst case acceptance value for attenuation when testing 2000 m (6562 ft) of 50/125 multimode fiber at a wavelength of 1300 nm when the fiber has 2 connector pairs and 3 splices?
The correct answer is C. 5.4 dB. See the full explanation below for the reasoning.
Question
What is the worst case acceptance value for attenuation when testing 2000 m (6562 ft) of 50/125 multimode fiber at a wavelength of 1300 nm when the fiber has 2 connector pairs and 3 splices?
Options
- A3.4 dB
- B4.65 dB
- C5.4 dB
- D6.4 dB
- E9.4 dB
How the community answered
(31 responses)- A6% (2)
- B16% (5)
- C74% (23)
- E3% (1)