HP0-S42 · Question #96
After sizing a rack with several ProLiant DL380p Gen9 servers running Windows Server 2008 R2 to use a redundant UPS Solution, a customer orders two HP UPS R7000s. What needs to be done to get this…
The correct answer is D. Configure the HP UPS Network Module for each R7000 UPS and HP Power manager software. See the full explanation below for the reasoning.
Question
After sizing a rack with several ProLiant DL380p Gen9 servers running Windows Server 2008 R2 to use a redundant UPS Solution, a customer orders two HP UPS R7000s. What needs to be done to get this UPS configuration working as a redundant UPS solution and gracefully shutdown Windows Server 2008 R2 when a power failure occurs at the input feed of both R7000 UPSs?
Options
- AConfigure the HP UPS Network Module for each R7000 UPS and HP Power Proactive software
- BConfigure the HP UPS Management Card for each R7000 UPS and HP power proactive software
- CConfigure the HP UPS Management Card for each R7000 UPS and HP Power manager software
- DConfigure the HP UPS Network Module for each R7000 UPS and HP Power manager software
How the community answered
(32 responses)- A3% (1)
- B9% (3)
- C6% (2)
- D81% (26)
Community Discussion
No community discussion yet for this question.