HP0-S42 · Question #89
A customer bought 30 ProLiant DL360p Gen9 with 750 watt Platinum Power Supplies. Due to space restrictions, this configuration needs to be installed in the smallest possible footprint. The maximum…
The correct answer is A. Use an HP 10642 G2 Rack with Top Exhaust Rack option. The HP Modular Cooling System G2 is the next generation self-cooled rack for high density deployments in the datacenter. HP's new Bi-Directional cooling technology makes possible the simultaneous cooling of two racks with a single MCS G2 unit. The MCS G2 racks can cool up to…
Question
A customer bought 30 ProLiant DL360p Gen9 with 750 watt Platinum Power Supplies. Due to space restrictions, this configuration needs to be installed in the smallest possible footprint. The maximum estimated heatload will be 22.5KW. The data center is designated for a maximum load of 8 KW per rack. What is the best solution?
Options
- AUse an HP 10642 G2 Rack with Top Exhaust Rack option
- BUse an HP 10842 G2 Rack with Rack Root Mount Fan option
- CUse an HP 10647 G2 Rack with Rack Airflow Optimization Kit Option
- DUse an HP Modular Cooling System G2
How the community answered
(27 responses)- A70% (19)
- B19% (5)
- C4% (1)
- D7% (2)
Explanation
The HP Modular Cooling System G2 is the next generation self-cooled rack for high density deployments in the datacenter. HP's new Bi-Directional cooling technology makes possible the simultaneous cooling of two racks with a single MCS G2 unit. The MCS G2 racks can cool up to 17.5kW per rack when cooling two racks or up to 35kW when cooling a single rack
Topics
Community Discussion
No community discussion yet for this question.