HH0-240 · Question #70
A customer is using an HUS 130 system as external storage behind an HUS VM. They are reworking the power distribution and need to power down both storage systems. What is the correct sequence of…
The correct answer is A. Stop the host I/O > power off the HUS VM > power off the HUS 130. See the full explanation below for the reasoning.
Question
A customer is using an HUS 130 system as external storage behind an HUS VM. They are reworking the power distribution and need to power down both storage systems. What is the correct sequence of actions?
Options
- AStop the host I/O > power off the HUS VM > power off the HUS 130.
- BStop the host I/O > power off the HUS 130 > power off the HUS VM.
- CPerform a path disconnect to the HUS 130 > stop the host I/O > power off the HUS 130 > power
- DStop the host I/O > perform a path disconnect to the HUS 130 > allow the storage systems to go
How the community answered
(34 responses)- A76% (26)
- B12% (4)
- C3% (1)
- D9% (3)