HAT-420 · Question #20

How should the Hitachi Unified Storage systems dual power supplies be connected?

The correct answer is D. by two independent and appropriately rated power distribution units. Dual power supplies must connect to two independent, appropriately rated PDUs (option D) to achieve true redundancy - if one PDU loses power due to a circuit fault, tripped breaker, or maintenance, the system continues running on the other. Option A is wrong because FS6 circuit…

Hardware Installation and Cabling

Question

How should the Hitachi Unified Storage systems dual power supplies be connected?

Options

  • Aby FS6 circuits breakers
  • Bonly one should be connected, the other being standby
  • Cby adjacent sockets on a single power distribution unit
  • Dby two independent and appropriately rated power distribution units

How the community answered

(26 responses)
  • A
    4% (1)
  • B
    8% (2)
  • D
    88% (23)

Explanation

Dual power supplies must connect to two independent, appropriately rated PDUs (option D) to achieve true redundancy - if one PDU loses power due to a circuit fault, tripped breaker, or maintenance, the system continues running on the other. Option A is wrong because FS6 circuit breakers are an unrelated switching/protection component, not a power distribution strategy. Option B defeats the purpose of dual supplies entirely; standby-only configurations introduce failover delay and a single point of failure during switchover. Option C is the most dangerous distractor - plugging both supplies into the same PDU means a single PDU failure takes down both supplies simultaneously, giving you zero redundancy despite having two units.

Memory tip: Think "dual supply = dual source." If both cables trace back to the same box (one PDU), you have one real power source wearing two hats - that's not redundancy, that's a false sense of security.

Topics

#dual power supply#PDU#redundant power#hardware installation