Using UPS5000-E (50kVA power module), the actual load is 160kW, the rack is 1+1 redundant, the single-machine backup power scheme is adopted, the backup power scheme for each machine, 3 sets of…
The correct answer is A. 630A. See the full explanation below for the reasoning.
Question
Using UPS5000-E (50kVA power module), the actual load is 160kW, the rack is 1+1 redundant, the single-machine backup power scheme is adopted, the backup power scheme for each machine, 3 sets of batteries per rack, 40 cells per set, the capacity of the main switch box is:
Options
- A630A
- B500A
- C250A
- D320A
How the community answered
(31 responses)- A84% (26)