The UPS can generate large leakage currents. A circuit breaker equipped with a residual current device (RCD) is not recommended. If leakage protection is required. consider the leakage current of…
The correct answer is A. True. See the full explanation below for the reasoning.
Question
The UPS can generate large leakage currents. A circuit breaker equipped with a residual current device (RCD) is not recommended. If leakage protection is required. consider the leakage current of the UPS and downstream devices.
Options
- ATrue
- BFalse
How the community answered
(47 responses)- A77% (36)
- B23% (11)