H12-425_V2.0 · Question #448

The power system of a UPS2000-4G-15K at a site is three-phase input and single-phase output. After installation, it is found that the mains and bypass inputs are three-phase, the output is…

The correct answer is A. The wing modes incorrect if the upstream mains input switch is turned on the UPS will be short-circuited. See the full explanation below for the reasoning.

Question

The power system of a UPS2000-4G-15K at a site is three-phase input and single-phase output. After installation, it is found that the mains and bypass inputs are three-phase, the output is single-phase, and the mains and bypass inputs share a power source. Which of the following statements are true about the UPS wiring mode?

Options

  • AThe wing modes incorrect if the upstream mains input switch is turned on the UPS will be short-circuited
  • BThe wiring mode is correct. The UPS can start properly.
  • CThe wing mode is incorrect. The UPS cannot wort in battery mode but can still work in bypass mode or
  • DThe wing modes incorrect. The correct wing mode should be single-phase bypass input three-phase

How the community answered

(37 responses)
  • A
    78% (29)
  • B
    8% (3)
  • C
    3% (1)
  • D
    11% (4)