The UPS system is configured with 32 12V batteries. What is the float charge voltage set for the UPS?
The correct answer is A. 432V. See the full explanation below for the reasoning.
Question
The UPS system is configured with 32 12V batteries. What is the float charge voltage set for the UPS?
Options
- A432V
- B451V
- C540V
- D564V
How the community answered
(30 responses)- A80% (24)
- B13% (4)
- C3% (1)
- D3% (1)