When the load is 60KW, the capacity of each UPS is 100KVA, and the power factor is 0.95, then when the system must be redundantly configured, at least () UPS are required.
The correct answer is A. 2. See the full explanation below for the reasoning.
Question
When the load is 60KW, the capacity of each UPS is 100KVA, and the power factor is 0.95, then when the system must be redundantly configured, at least () UPS are required.
Options
- A2
How the community answered
(28 responses)- A100% (28)