DU0-001 · Question #46

What allows you to support single-corded loads in a 2N UPS redundant configuration?

The correct answer is B. Transfer switch. A transfer switch, specifically an automatic transfer switch (ATS), solves the fundamental problem of single-corded loads in a 2N UPS configuration: it connects to both redundant UPS paths (A and B) and automatically switches the load to the healthy path if one fails, giving a…

Power Systems in the Data Center

Question

What allows you to support single-corded loads in a 2N UPS redundant configuration?

Options

  • ADC disconnect
  • BTransfer switch
  • CStatic bypass switch
  • DWrap around external bypass

How the community answered

(54 responses)
  • A
    4% (2)
  • B
    80% (43)
  • C
    6% (3)
  • D
    11% (6)

Explanation

A transfer switch, specifically an automatic transfer switch (ATS), solves the fundamental problem of single-corded loads in a 2N UPS configuration: it connects to both redundant UPS paths (A and B) and automatically switches the load to the healthy path if one fails, giving a single-cord device the same redundancy benefit as a dual-corded device. A DC disconnect (A) is used to isolate the battery bank from UPS circuitry for safety or maintenance and plays no role in routing power to loads. A static bypass switch (C) reroutes load power around the UPS internals to utility power during a fault or maintenance window - it protects the UPS, not the load's redundancy path. A wrap around external bypass (D) similarly allows the entire UPS to be bypassed for servicing and does not address how a single-corded device connects to two separate UPS feeds.

Memory tip: A transfer switch transfers the power source - it moves a single-cord device between two redundant paths, bridging the gap that a single cord cannot span on its own.

Topics

#2N UPS#single-corded loads#transfer switch#redundant configuration