code jurisdiction mandates a sprinkler system in the data center.How can you further protect the data center's IT equipment while meeting the mandated requirements?
The correct answer is B. Replace the wet-pipe sprinkler system with a pre-action system. Pre-action sprinkler systems are the best solution because they satisfy the code mandate for a sprinkler system while adding a crucial layer of protection: water only flows when two independent events occur - a fire detector activates AND a sprinkler head opens. This two-stage…
Question
Options
- AReplace the wet-pipe sprinkler system with a FM-200 system.
- BReplace the wet-pipe sprinkler system with a pre-action system.
- CInstall linear heat detectors along the cable trays in addition to the existing sprinkler system
- DInstall heat detectors next to each of the sprinkler heads and then connect them to the fire control panel.
How the community answered
(49 responses)- A2% (1)
- B80% (39)
- C12% (6)
- D6% (3)
Explanation
Pre-action sprinkler systems are the best solution because they satisfy the code mandate for a sprinkler system while adding a crucial layer of protection: water only flows when two independent events occur - a fire detector activates AND a sprinkler head opens. This two-stage mechanism prevents accidental water discharge (e.g., from a broken sprinkler head), which is the primary threat to IT equipment in a data center.
Option A is wrong because FM-200 is a gaseous suppression agent, not a sprinkler system - replacing the wet-pipe system with FM-200 would violate the code mandate, regardless of how effective FM-200 is for protecting electronics.
Option C is wrong because linear heat detectors are detection devices, not suppression - they detect heat in cable trays but do nothing to prevent water from damaging equipment when the existing wet-pipe system activates.
Option D is wrong because adding heat detectors next to sprinkler heads only improves alarm notification; it does not change the wet-pipe system's behavior. Water still sits pressurized in the pipes and releases the moment any head opens - accidentally or not.
Memory tip: Think "Pre-action = Protection Action." A pre-action system demands a deliberate action (detector trigger) before water is admitted to the pipes - it won't soak your servers by accident.