D-PE-OE-23 · Question #18

A server is configured in a 1+1 power configuration with both PSUs connected to a single PDU. Which redundancy options does this configuration supply?

The correct answer is A. PSU redundancy only. Option A is correct because a 1+1 configuration provides PSU redundancy only - if one power supply fails, the other takes over, keeping the server running. However, since both PSUs feed from the same PDU, a PDU failure kills power to both PSUs simultaneously, meaning there is…

PowerEdge Components and Architecture

Question

A server is configured in a 1+1 power configuration with both PSUs connected to a single PDU. Which redundancy options does this configuration supply?

Options

  • APSU redundancy only
  • BPSU redundancy and PDU redundancy
  • CNo redundancy unless each PSU is connected to a separate PDU
  • DPSU redundancy and Grid redundancy

How the community answered

(46 responses)
  • A
    67% (31)
  • B
    4% (2)
  • C
    20% (9)
  • D
    9% (4)

Explanation

Option A is correct because a 1+1 configuration provides PSU redundancy only - if one power supply fails, the other takes over, keeping the server running. However, since both PSUs feed from the same PDU, a PDU failure kills power to both PSUs simultaneously, meaning there is no PDU redundancy.

Why the distractors are wrong:

  • B is wrong because PDU redundancy requires each PSU to connect to a separate PDU; a single shared PDU is a single point of failure.
  • C is wrong because PSU redundancy does exist even with one PDU - the 1+1 setup handles PSU-level failures just fine; it's only PDU-level failures that aren't covered.
  • D is wrong because grid redundancy requires two independent power feeds (e.g., from separate utility sources or UPS systems), which is a completely different layer not addressed here.

Memory tip: Think in layers - PSU protects against unit failure, PDU protects against distribution failure, and grid protects against source failure. Each layer needs its own redundant path; sharing a PDU collapses the PSU and PDU layers into one point of failure.

Topics

#PSU redundancy#PDU#1+1 power configuration#fault tolerance