nerdexam
EXIN

CDCP · Question #21

A fire extinguisher in the data centre is found which is classed as ABC. Is this suitable?

The correct answer is D. No. A fire extinguisher in the data centre that is classed as ABC is not suitable, because it contains dry chemical powder that can damage the ICT equipment and the data. ABC fire extinguishers are designed to fight Class A, B, and C fires, which are fueled by combustible…

Fire Suppression

Question

A fire extinguisher in the data centre is found which is classed as ABC. Is this suitable?

Options

  • AYes
  • BDepends on the brand
  • COnly for fires not related to electrical power
  • DNo

How the community answered

(28 responses)
  • A
    4% (1)
  • C
    4% (1)
  • D
    93% (26)

Explanation

A fire extinguisher in the data centre that is classed as ABC is not suitable, because it contains dry chemical powder that can damage the ICT equipment and the data. ABC fire extinguishers are designed to fight Class A, B, and C fires, which are fueled by combustible materials, flammable liquids or gases, and electrical equipment, respectively. However, the dry chemical powder can leave a corrosive residue on the ICT equipment, which can cause short circuits, data loss, or malfunction. Moreover, the dry chemical powder can be difficult to clean, especially from the small spaces and crevices of the ICT equipment. Therefore, ABC fire extinguishers are not recommended for data centres, and should be replaced with more suitable fire extinguishers, such as clean agent fire extinguishers, which use gas or liquid that does not leave any residue or harm the ICT equipment.

Topics

#ABC extinguisher#electrical fire#fire suppression suitability#extinguisher classification

Community Discussion

No community discussion yet for this question.

Full CDCP Practice